  1. I'm not an HVAC tech, but I am a retired electrician.

     

    1st step I'd take is to use a voltmeter to check for voltage at the relay coil terminals. Since you are using DC you need to make sure you have correct polarity at the relay coil.

    If you have correct voltage and polarity at the coil, and the coil does not operate, then the coil is defective. If the polarity is incorrect, reverse the wires at the coil. If the voltage is not correct, at the relay coil, then you have a problem with the control circuit.

     

    Make sure the stat contacts are rated for DC current (most are rated for 24 VAC). When I have done projects using these types of stats I always used relays with 24VAC coils. DC current is much harder on contacts than AC current.

     

    Good Luck

×
×