This is a follow up to some research after an extension cord fire caught me off guard.  Don't let this happen to you!  Update your AFCI breakers or add one...

 

205be6d2ccc00c66304608d71c105e87.jpg

 

 

Background:  

 

First off, from this link:

 

http://www.leviton.com/OA_HTML/SectionDisplay.jsp?section=61255

 

1) What is an arc-fault?

The UL Standard for AFCIs defines an arc-fault as an unintentional arcing condition in a circuit (wiring). Arcing creates high intensity heat (may exceed 10,000 degrees Fahrenheit) resulting in burning particles that may over time ignite surrounding material such as wood framing or insulation. Samples of types of arcing that can occur:
 
 

2) What causes an arc-fault?

There are a wide range of conditions that may cause arcing.

ibcGetAttachment.jsp?cItemId=FvWk2-v0740Wire Degradation
  • Natural degradation through age
  • Humidity or heat
  • Extended mechanical stress
  • Extended voltage stress
Physical Damage
  • Animals chewing through insulation
  • Nails, tacks from construction or picture hanging driven into a wall puncturing or damaging a wire(s)
  • Extension or power supply cord damage from sharp bends or furniture pressing on or against cords
  • General cord damage
  • Poor wiring or connection at devices/j-boxes

 

Solution:

 

Even if your home has AFCI breakers, if they are from before 2008 they won't protect against series arcs.  

 

34063d1404321037-what-cafci-breaker-seri

 

Consider having your breakers updated, at least in the room where the aquariums are!

 

 

 

Don't let this happen to you (I watched this plug erupt in flame after a quick jiggle...)

 

 

  • Like 4
  • Thanks 1
Link to comment
Share on other sites

Other things I personally am doing:

 

- adding a Z-wave compatible smoke detector right above the tank wiring.  With ZWave, I can use a home automation controller to text me if there is any smoke at all or even turn off all the outlet itself.

- Replacing all extension cords (corrosion)

- Looking into CRC for plugs/receptacles to prevent further corrosion

- Tossed my slightly rusty light reflectors over fuge, replaced with cheap D120 light (splashproof and DC current)

 

pretty much anything that might make a difference.

 

But the big one IMO was the fact that the AFCI did not trip, I have been counting on it.

  • Like 2
Link to comment
Share on other sites

Added the combination AFCI adapter this morning.

 

Very thankful it did not trip, I have no other arc faults so far that it knows about.

 

It looks like the are required by code after 2014.

 

Truly believe this would have tripped, wish I could test it though other than the test button!

 

Going to replace all of the existing AFCIs moving forward.

 

ZWave smoke detector going in today as well by all the plugs.

Link to comment
Share on other sites

So wait - I want to replace the circuit in my breaker box to an AFCI if it isn't already? I was also going to run a GFCI on the outlet going to the tank. Is that something you'd recommend? 

Link to comment
Share on other sites

GFCI to protect from shock, Combination AFCI to protect from fire.

 

Combination AFCI (CAFCI) typically in the panel.  GFCI ideally I prefer on each outlet for each device in the tank.  You can do one GFCI, but they do trip.  A GFCI per outlet makes that a localized event so that not everything shuts down.

 

If your AFCI is not very new, it is probably not CAFCI.  My AFCI did not trip on the serial arc, the CAFCI is supposed to.

 

Just my opinions of course, not an expert.  Sharing to spur others to research their options and be aware of the fire hazard.

Link to comment
Share on other sites

Thanks John.  Today we had a nuisance trip in the family room cafci, breaker diagnostics said it was an arc fault.  

 

So.... my personal jury is out on these if the nuisance trips become an issue.  Heck, maybe I really do have an arc fault?

 

Took the breakers out and double checked everything was properly and well secured, seemed good.

 

Time will tell, just sharing for those interested...

Link to comment
Share on other sites

  • 1 year later...

Nuisance trips are a thing of the past.  Through process of elimination we found the sources and eliminated them.  They were legit trips and perhaps in theory prevented a fire...  I wish I could remember what they were though...

Link to comment
Share on other sites

3 minutes ago, HenryLimpet said:

Great Thread, I just built my home and it is loaded with smoke detectors (code requirements in Clark county). So I just purchased a Leeo smart alert. It plugs into a wall outlet and listens for detectors going off, then send a text.

That is cool, gotta check that out!

 

Link to comment
Share on other sites

10 minutes ago, Ninjabeaver said:

Well what circuits are they required on? My panel has only two fancy breakers and they cover they bedrooms.


Sent from the bottom of the sea.

I am sure not the right guy to ask about electrical codes....  It used to be just bedrooms if I understand right, but has slowly grown to more living spaces.

Link to comment
Share on other sites

I am sure not the right guy to ask about electrical codes....  It used to be just bedrooms if I understand right, but has slowly grown to more living spaces.


So I kept having one of the fancy breakers trip for no reason, my electrician friend checked it out couldn't find any reason for it, even when every switch and light was on in the house the load on that circuit was not even close to capacity.

So he replaced it with a regular breaker and no problems since.

He was saying that in the electrical world there are some dumb codes, and lobbying to get requirements passed that make it more expensive in the industry, paid for by the companies that produce the products nessesary to comply with the code.

All that said, I really don't want any of our houses to burn down.


Sent from the bottom of the sea.
Link to comment
Share on other sites

1 minute ago, Ninjabeaver said:

 


So I kept having one of the fancy breakers trip for no reason, my electrician friend checked it out couldn't find any reason for it, even when every switch and light was on in the house the load on that circuit was not even close to capacity.

So he replaced it with a regular breaker and no problems since.

He was saying that in the electrical world there are some dumb codes, and lobbying to get requirements passed that make it more expensive in the industry, paid for by the companies that produce the products nessesary to comply with the code.

All that said, I really don't want any of our houses to burn down.


Sent from the bottom of the sea.

 

It's true.  However that smoked extension cord was an eye opener for me.

My nuisance trips were legit.  Partially plugged in extension cord, Christmas lights etc.  Once I chased all those down.. None since.

Here is some good info on a wall installable afci (like a gfci)

http://www.leviton.com/en/products/electrical-wiring-devices/arcfault-circuit-interrupters-afcis

Personally I never want to have to say 'Sorry kids, daddies reef tank burnt down the house and all your toys and pets'!

A little extreme but this was a big event for me!

 

  • Like 1
Link to comment
Share on other sites

It's true.  However that smoked extension cord was an eye opener for me.
My nuisance trips were legit.  Partially plugged in extension cord, Christmas lights etc.  Once I chased all those down.. None since.
Here is some good info on a wall installable afci (like a gfci)
http://www.leviton.com/en/products/electrical-wiring-devices/arcfault-circuit-interrupters-afcis
Personally I never want to have to say 'Sorry kids, daddies reef tank burnt down the house and all your toys and pets'!
A little extreme but this was a big event for me!
 


Ya not a good situation, I had my dj power strip burnup last year with a lot of smoke, almost forgot about that, it was corroded and salt creep and gotten into the unit.


Sent from the bottom of the sea.
Link to comment
Share on other sites

Just now, Ninjabeaver said:

 


Ya not a good situation, I had my dj power strip burnup last year with a lot of smoke, almost forgot about that, it was corroded and salt creep and gotten into the unit.


Sent from the bottom of the sea.

 

Good point.  That salt creep is fire causing stuff!

 

Link to comment
Share on other sites

I thought that Afci were only required by code for bathrooms? I built a new bathroom in my old house and I had to put an Afci breaker on it. cost me $120 back then but they are way cheaper now.

good insurance for sure but they can be a major PIA. As I remember they measure the difference in current between neutral and hot and trip if there is a difference. so simply plugging things in can trip them or automated relay driving devices can also occasionally throw them... dishwasher, clothes washer, etc.

people think GFCI is the gold standard and it absolutely is not. it WILL prevent you from shocking yourself when a water pump looses ground (been there). But if there is a short, water on plugs, salt creep, drive a nail through the wire in the wall, rodent eating wire in the wall... the GFCI does nothing.

I am not an electrician but have done complete rewires of two separate houses and also installed a very very very complicated wiring project at my company that involved maxing out two 700 amp 3 phase power feeds. You want to get nervous about fiddling around with electricity I'll give you a tour of our facility. lol. I put huge signs on the 480 disconnects "DON'T EVEN THINK ABOUT OPENING THIS".


Sent from my SM-G930V using Tapatalk

Link to comment
Share on other sites

3 hours ago, pdxmonkeyboy said:

I thought that Afci were only required by code for bathrooms? I built a new bathroom in my old house and I had to put an Afci breaker on it. cost me $120 back then but they are way cheaper now.

good insurance for sure but they can be a major PIA. As I remember they measure the difference in current between neutral and hot and trip if there is a difference. so simply plugging things in can trip them or automated relay driving devices can also occasionally throw them... dishwasher, clothes washer, etc.

people think GFCI is the gold standard and it absolutely is not. it WILL prevent you from shocking yourself when a water pump looses ground (been there). But if there is a short, water on plugs, salt creep, drive a nail through the wire in the wall, rodent eating wire in the wall... the GFCI does nothing.

I am not an electrician but have done complete rewires of two separate houses and also installed a very very very complicated wiring project at my company that involved maxing out two 700 amp 3 phase power feeds. You want to get nervous about fiddling around with electricity I'll give you a tour of our facility. lol. I put huge signs on the 480 disconnects "DON'T EVEN THINK ABOUT OPENING THIS".


Sent from my SM-G930V using Tapatalk
 

Gfci would be for a bathroom by code requirement also code now requires afci in all dwelling units. 

Here's a pic of code articles faster than typing it out. I don't do alot of residential so it's not on the top of my head. 

20170404_222702.jpg

20170404_222737.jpg

  • Like 1
Link to comment
Share on other sites

1 minute ago, TheClark said:

Good info @Vance164, thanks!

 

No problem this is from 2014 code because I haven't tabbed my 2017 since I just got it last week but there isn't any major changes since then on the subject since afci is highlighted grey it was all new code added to that cycle. 

Link to comment
Share on other sites

17 hours ago, pdxmonkeyboy said:


good insurance for sure but they can be a major PIA. As I remember they measure the difference in current between neutral and hot and trip if there is a difference. so simply plugging things in can trip them or automated relay driving devices can also occasionally throw them... dishwasher, clothes washer, etc.


 

Interesting info.  This could definitely lead to a lot of false positives but I can see the logic (from a safety protection standpoint).

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...