So I picked up a used Apex system a few days ago, and for the most part I have it figured out but,... several times a day I get an email and text from the unit. The messages are similar to this:

Date: 2015-08-22 08:49:00 (2015-08-22 15:49:00 UTC)

Status: ON

Statement: If Temp < 77.0 Then ON (75.6 )

 

This is how I have it set:

Fallback On

Set off

If Temp <77 Then On

If Temp >78 Then Off

 

Im sure it is an easy fix, but I cant figure it out. Thanks in advance.

Link to comment
Share on other sites

You also might want to use the control type "Heater" instead of advanced for the heaters outlet. But if your temp probe is calibrated and accurate, that email is saying your water temp is 75. If that's true and your heater is set to come on at 77, you might check if your heater is working correctly also.

Link to comment
Share on other sites